Let's test the real power saving on PTX platforms achieved when shutting down used and unused Packet Forwarding Engine (PFE).
Introduction
Power efficiency is key in today’s ever-growing Service providers and Cloud providers networks. Network industry improved the power and carbon footprint over the years through real innovations in silicon: manufacturing process, various components integration on the die and the package, monitoring and manageability.
PTX routers offer the granular control of individual PFE without impacting the other units present on the line card or the system. Operators can power on, power off and restart them at will, saving significant amount of energy.
In this article, we will detail:
- the multiple ways to power off PFEs manually and how to configure the system to take actions on PFE in case of error
- the power saving achieved turning off PFEs on an LC1201 in a PTX10016 with DR4 inserted and without affecting the traffic flowing on other ASICs of the card
- the power saving achieved turning off PFE on LC1201 in the three chassis types (PTX10004, PTX10008 and PTX10016) but also on fixed platforms like PTX10001-36MR, all of them without any optics inserted
Scope: we will not cover other Juniper platforms (MX/ACX/QFX/EX/…), only PTX.
PFE Power Off and Error Action
Packet Forward Engine are at the heart of our routing devices. Routers and Line Cards contains one or several of them. Multiple PFEs are interconnected via a switch fabric and fabric SerDes.
We can imagine multiple situations where you would like to turn off a PFE.
The first one is obvious: when PFEs are not in use. That could be the case if you use Pay As You Grow (PAYG) model with just a portion of the system/linecard capability. Or you didn't provisioned all ports yet and you strategicaly positioned your current ports to keep one or several PFE unused. Turning these unused PFEs off will reduce the system power consumption.
A second use-case would be to power off specific PFEs during periods of low traffic, usually at night. Traffic engineering rules will make sure no packets traverse these PFEs, and you can automate their power off to save energy for a couple of hours.
Let’s take for example a PTX10001-36MR to illustrate these scenarios
- with optics connected and forwarding traffic on PFE0
- without any optic modules on PFE1
- with optics connected but no traffic on PFE2
Diagram 1: PTX10001-36MR Block Diagram
Several power saving features are activated by default on PTX:
- Empty ports SerDes are shutdown (example: et-0/0/0)
- Gearboxes with only empty ports are kept in reset mode, SerDes to the PFE and to the optic cages are shutdown (example: ports et-0/1/4 to et-0/1/7)
The network operator can decide to go further than the default behavior and shutdown / power off the PFE1, since no ports are using it. That's our first use-case described above.
Diagram 2: PTX10001-36MR with PFE1 Powered Off
That's the tests we will perform on various chassis and fixed platform in the second part of this article. It will give us a good idea of the saving we can get from the PFE only (since the ports, gearboxes and SerDes are shutdown already).
Some users could decide to go even further and power off PFE2 (with optics but no traffic):
Diagram 3: PTX10001-36MR with PFE1 and PFE2 Powered Off
Of course, all ports on PFE1 and PFE2 disappeared and will only be restored after we turn the PFEs on again.
These are the tests we will run on the first part of this techpost, specifically on a PTX10016 and LC1201. It will give us an idea of the savings achieved with optics, SerDes and PFE being turned off.
We picked the PTX10001-36MR for illustration of the use-cases but it's equally applicable for other PTX10003 and PTX10k chassis and line cards.
Supported Platforms
The handling of PFEs independently of the FPC (and other PFEs) is available in Junos EVO-only platforms and the Table1 below displays the first releases supporting this feature.
Line Card |
Number of PFEs |
Platform |
Supported Release |
FPC-JNP10003 |
80C - 8 160C - 16 |
PTX10003-80C PTX10003-160C
|
20.4R1-EVO |
JNP10K-LC1201 |
5 |
PTX10008 |
21.2R1-EVO |
JNP10K-LC1201 |
5 |
PTX10004/PTX10016 |
21.4R1-EVO |
JNP10K-LC1202 |
2 |
PTX10004/10008/10016 |
21.4R1-EVO |
FPC-JNP10001-36MR |
3 |
PTX10001-36MR |
22.3R1-EVO |
Table 1: Supported Hardware and Software release
PFE States
Here are the possible PFE states which can be observed by running the CLI command “show chassis fpc pfe-instances all”
PFE State |
Description |
ONLINE |
PFE is Online |
Configured Power Off |
PFE is Offline via Configuration on router |
Offlined by CLI |
PFE Offline via Request CLI operation by user on router |
Offlined by CMError |
PFE Offline via CMError Action |
Transition_OFFLINE |
PFE Transition status |
FAULT |
When “disable-pfe” CMError action is taken by the Router on Major/Fatal errors |
PowerOn |
PFE state during PFE power on transition |
RESYNC |
This is the state when the PFE is synchronizing the state with other components withing the system |
READY |
When the PFE is ready after power on but not online yet. Takes a few more seconds to bring up online |
Table 2: PFE States
PFE Power Off
We will carry out tests on Express4-based PTX platforms: modular chassis (4, 8 and 16 slots) with 36x400GE LC1201 linecards, and on PTX10001-36MR fixed router. Routers were running Junos EVO versions: 22.4R2.11-EVO and 23.2R1.15-EVO
Configuration and CLI
PFE can be independently Powered off/on using Configuration mode or Operational (CLI) mode.
Below Table 3 shows the support of this feature across the platforms.
Mode |
PTX10004 |
PTX10008 |
PTX10016 |
PTX10001-36MR |
PTX10003-80C |
PTX10003-160C |
Config |
√ |
√ |
√ |
√ |
√ |
√ |
CLI |
√ |
√ |
√ |
√ |
X |
X |
Table 3: Platforms Support for PFE Power On/Off
Configuration Method
ptx10k16-01# set chassis fpc 0 pfe 0 power ?
Possible completions:
off Power off PFE
on Power on PFE
ptx10k16-01# set chassis fpc 0 pfe 0 power off
ptx10k16-01# commit
CLI Method
ptx10k16-01> request chassis fpc slot 0 pfe-instance 0 ?
Possible completions:
no-forwarding No forwarding
offline Take FPC or PFE-instance offline
online Bring FPC or PFE-instance online
restart Restart FPC or PFE-instance
tag Firmware tag for online-reload
ptx10k16-01> request chassis fpc slot 0 pfe-instance 0 offline
Fru Block offline initiated!
ptx10k16-01>
The “operation” CLI methods doesn’t need to commit a configuration, which could be an advantage is certain cases.
Regardless the method, it takes less than 5s to transition to offline state.
Test1: PFE PowerOff/Offline with Optics and Traffic
In this first test, we will apply the two methods for two PFEs 0 and 1, and we will verify it does not impact other PFEs in the system.
We will use a LC1201 in a PTX10016 (16-slot chassis), offering 36 ports 400GE and based of 5x Express4. Each PFE package contains itself two datapaths.
All ports are populated with DR4 optics but only the last 20 are connected to a traffic generator pushing 50% full-meshed traffic, 512 bytes per packet.
Diagram 4: Test 1 Topology with LC1201, DR4 Optics and Traffic on PFE2/3/4
ptx10k16-01> show interfaces terse
Interface Admin Link Proto Local Remote
et-0/0/0 up up
et-0/0/0.0 up up inet 100.1.1.1/24
multiservice
pfh-0/0/0 up up
pfh-0/0/0.16383 up up inet
et-0/0/2 up up
et-0/0/2.0 up up inet 100.1.3.1/24
multiservice
et-0/0/4 up up
et-0/0/4.0 up up inet 100.1.5.1/24
multiservice
et-0/0/6 up up
et-0/0/6.0 up up inet 100.1.7.1/24
multiservice
et-0/0/8 up up
et-0/0/8.0 up up inet 100.1.9.1/24
multiservice
et-0/0/10 up up
et-0/0/10.0 up up inet 100.1.11.1/24
multiservice
et-0/0/12 up up
et-0/0/12.0 up up inet 100.1.13.1/24
multiservice
et-0/0/14 up up
et-0/0/14.0 up up inet 100.1.15.1/24
multiservice
et-0/0/16 up up
et-0/0/16.0 up up inet 100.1.17.1/24
multiservice
et-0/0/17 up up
et-0/0/17.0 up up inet 100.1.18.1/24
multiservice
et-0/0/18 up up
et-0/0/18.0 up up inet 100.1.19.1/24
multiservice
et-0/0/19 up up
et-0/0/19.0 up up inet 100.1.20.1/24
multiservice
et-0/0/20 up up
et-0/0/20.0 up up inet 100.1.21.1/24
multiservice
et-0/0/21 up up
et-0/0/21.0 up up inet 100.1.22.1/24
multiservice
et-0/0/22 up up
et-0/0/22.0 up up inet 100.1.23.1/24
multiservice
et-0/0/23 up up
et-0/0/23.0 up up inet 100.1.24.1/24
multiservice
et-0/0/24 up up
et-0/0/24.0 up up inet 100.1.25.1/24
multiservice
et-0/0/25 up up
et-0/0/25.0 up up inet 100.1.26.1/24
multiservice
et-0/0/26 up up
et-0/0/26.0 up up inet 100.1.27.1/24
multiservice
et-0/0/27 up up
et-0/0/27.0 up up inet 100.1.28.1/24
multiservice
et-0/0/28 up up
et-0/0/28.0 up up inet 100.1.29.1/24
multiservice
et-0/0/29 up up
et-0/0/29.0 up up inet 100.1.30.1/24
multiservice
et-0/0/30 up up
et-0/0/30.0 up up inet 100.1.31.1/24
multiservice
et-0/0/31 up up
et-0/0/31.0 up up inet 100.1.32.1/24
multiservice
et-0/0/32 up up
et-0/0/32.0 up up inet 100.1.33.1/24
multiservice
et-0/0/33 up up
et-0/0/33.0 up up inet 100.1.34.1/24
multiservice
et-0/0/34 up up
et-0/0/34.0 up up inet 100.1.35.1/24
multiservice
et-0/0/35 up up
et-0/0/35.0 up up inet 100.1.36.1/24
multiservice
ptx10k16-01> show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 ONLINE
1 ONLINE
2 ONLINE
3 ONLINE
4 ONLINE
ptx10k16-01> show chassis pic fpc-slot 0 pic-slot 0
FPC slot 0, PIC slot 0 information:
Type JNP10K-36QDD-LC-PIC
State Online
PIC version 00.00
Uptime 15 hours, 44 minutes, 25 seconds
Port speed information:
Port PFE Capable Port Speeds
0 1 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
1 0 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
2 1 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
3 0 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
4 1 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
5 0 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
6 1 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
7 0 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
8 1 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
9 0 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
10 1 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
11 0 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
12 1 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
13 0 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
14 1 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
15 0 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
16 3 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
17 2 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
18 3 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
19 2 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
20 3 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
21 2 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
22 3 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
23 2 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
24 3 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
25 2 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
26 3 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
27 2 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
28 3 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
29 2 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
30 3 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
31 2 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
32 4 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
33 4 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
34 4 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
35 4 1x10G 4x10G 1x40G 4x25G 1x100G 2x50G 2x100G 3x100G 4x100G 1x400G
ptx10k16-01>
---
ptx10k16-01-fpc0:pfe> show pfe id info
First Active PFE : 0
Effective First Active PFE : 0
Number of Active PFEs : 5
Pfe Mask : 0x000000000000001f
PFEInst Down-Flags PPFE-ID PFE-State PFE-Name
------ ---------- ------------- --------- --------
0 0 0 ONLINE /Chassis[0]/Fpc[0]/Pfe[0]
0 0 1 ONLINE /Chassis[0]/Fpc[0]/Pfe[1]
1 0 2 ONLINE /Chassis[0]/Fpc[0]/Pfe[2]
1 0 3 ONLINE /Chassis[0]/Fpc[0]/Pfe[3]
2 0 4 ONLINE /Chassis[0]/Fpc[0]/Pfe[4]
2 0 5 ONLINE /Chassis[0]/Fpc[0]/Pfe[5]
3 0 6 ONLINE /Chassis[0]/Fpc[0]/Pfe[6]
3 0 7 ONLINE /Chassis[0]/Fpc[0]/Pfe[7]
4 0 8 ONLINE /Chassis[0]/Fpc[0]/Pfe[8]
ptx10k16-01-fpc0:pfe>
The output of “show chassis pic fpc-slot 0 pic-slot 0” gives us the mapping of ports to PFE in the LC1201 and “show pfe id info” under CLI-PFE details the PFE instances.
Before starting the test, we check system power consumption:
ptx10k16-01> show chassis power detail
Chassis Power Voltage(V) Power(W)
<SNIP>
Item Used(W)
CB 0 97
CB 1 83
FPC 0 1380
SIB 0 499
SIB 1 511
SIB 2 514
SIB 3 502
SIB 4 499
SIB 5 500
Fan Tray 0 1035
Fan Tray 1 1043
System:
Zone 0:
Capacity: 10800 W (maximum 22000 W)
Allocated power: 9370 W (1430 W remaining)
Actual usage: 7416 W
Total system capacity: 10800 W (maximum 22000 W)
Total remaining power: 1430 W
We configured streaming telemetry and Grafana dashboards to display the power usage in real time. Note that it's a better approach that simply capturing the out of "show chassis power detail" since the numbers are always slightly fluctuating:
Diagram 5: Power Usage Representation through Streaming Telemetry
And the traffic generator shows:

Diagram 6: Traffic Generator Snapshot, 20 Ports at 50% Load
First method applied on PFE0 is via configuration:
ptx10k16-01# set chassis fpc 0 pfe 0 power off
ptx10k16-01# commit
ptx10k16-01# run show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 TRANSITION_OFFLINE
1 ONLINE
2 ONLINE
3 ONLINE
4 ONLINE
ptx10k16-01# run show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 Configured power off
1 ONLINE
2 ONLINE
3 ONLINE
4 ONLINE
Diagram 7: Test1 Topology with PFE0 Configured Powered Off
We check power usage:
ptx10k16-01> show chassis power detail
Chassis Power Voltage(V) Power(W)
<SNIP>
Item Used(W)
CB 0 86
CB 1 79
FPC 0 1133
SIB 0 490
SIB 1 501
SIB 2 505
SIB 3 491
SIB 4 492
SIB 5 496
Fan Tray 0 1034
Fan Tray 1 1045
System:
Zone 0:
Capacity: 10800 W (maximum 22000 W)
Allocated power: 9370 W (1430 W remaining)
Actual usage: 7152 W
Total system capacity: 10800 W (maximum 22000 W)
Total remaining power: 1430 W
This is reflected on the Grafana for the FPC0:
Diagram 8: Power Saving on FPC0 with PFE0 Offline
Note: these 247W of power saving include ports and SerDes, not only "PFE offline". That’s why we will perform the same tests without any optics in the second part of this article.
Diagram 9: Power Saving on SIBs with PFE0 Offline
We will explain below why we are seeing also power saving on the fabric side when powering off a PFE.
We don’t see any impact on the traffic flowing through PFE2, PFE3 and PFE4.
Second method applied to PFE1 with CLI:
ptx10k16-01> request chassis fpc slot 0 pfe-instance 1 offline
Fru Block offline initiated!
ptx10k16-01> show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 Configured power off
1 TRANSITION_OFFLINE
2 ONLINE
3 ONLINE
4 ONLINE
ptx10k16-01> show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 Configured power off
1 Offlined by CLI
2 ONLINE
3 ONLINE
4 ONLINE
We clearly see the difference in PFE-State based on the two methods, but the result in term of power saving is the same. In these states, the PFEs consume a negligeable amount of energy.
Diagram 10: Test1 Topology with PFE0 and PFE1 Configured Powered Off / Offline
We verify again the power usage:
ptx10k16-01> show chassis power detail
Chassis Power Voltage(V) Power(W)
<SNIP>
Item Used(W)
CB 0 86
CB 1 79
FPC 0 884
SIB 0 480
SIB 1 488
SIB 2 494
SIB 3 480
SIB 4 480
SIB 5 484
Fan Tray 0 1023
Fan Tray 1 1046
System:
Zone 0:
Capacity: 10800 W (maximum 22000 W)
Allocated power: 9370 W (1430 W remaining)
Actual usage: 6840 W
Total system capacity: 10800 W (maximum 22000 W)
Total remaining power: 1430 W
Diagram 11: Power Saving on FPC0 with PFE1 Offline
Same level of savings with the second method, which is totally aligned with our expectations.
And here again, we are seeing savings on the Fabric Cards.
Diagram 12: Power Saving on SIBs with PFE1 Offline
With PFE0 and PFE1 powered off, all interfaces mapped to them logically disappeared.
ptx10k16-01> show interfaces terse
Interface Admin Link Proto Local Remote
pfh-0/0/0 up up
pfh-0/0/0.16383 up up inet
et-0/0/16 up up
et-0/0/16.0 up up inet 100.1.17.1/24
multiservice
et-0/0/17 up up
et-0/0/17.0 up up inet 100.1.18.1/24
multiservice
et-0/0/18 up up
et-0/0/18.0 up up inet 100.1.19.1/24
multiservice
et-0/0/19 up up
et-0/0/19.0 up up inet 100.1.20.1/24
multiservice
et-0/0/20 up up
et-0/0/20.0 up up inet 100.1.21.1/24
multiservice
et-0/0/21 up up
et-0/0/21.0 up up inet 100.1.22.1/24
multiservice
et-0/0/22 up up
et-0/0/22.0 up up inet 100.1.23.1/24
multiservice
et-0/0/23 up up
et-0/0/23.0 up up inet 100.1.24.1/24
multiservice
et-0/0/24 up up
et-0/0/24.0 up up inet 100.1.25.1/24
multiservice
et-0/0/25 up up
et-0/0/25.0 up up inet 100.1.26.1/24
multiservice
et-0/0/26 up up
et-0/0/26.0 up up inet 100.1.27.1/24
multiservice
et-0/0/27 up up
et-0/0/27.0 up up inet 100.1.28.1/24
multiservice
et-0/0/28 up up
et-0/0/28.0 up up inet 100.1.29.1/24
multiservice
et-0/0/29 up up
et-0/0/29.0 up up inet 100.1.30.1/24
multiservice
et-0/0/30 up up
et-0/0/30.0 up up inet 100.1.31.1/24
multiservice
et-0/0/31 up up
et-0/0/31.0 up up inet 100.1.32.1/24
multiservice
et-0/0/32 up up
et-0/0/32.0 up up inet 100.1.33.1/24
multiservice
et-0/0/33 up up
et-0/0/33.0 up up inet 100.1.34.1/24
multiservice
et-0/0/34 up up
et-0/0/34.0 up up inet 100.1.35.1/24
multiservice
et-0/0/35 up up
et-0/0/35.0 up up inet 100.1.36.1/24
multiservice
ptx10k16-01>
And no impact on the neighbor PFEs:
Diagram 13: Traffic Generator Showing Same Traffic Load
Now let’s rollback and power on these two PFEs using the two different methods (we can see the different states during the booting phases).
Logically, if you powered off PFE0 via configuration, you will need to power it on via configuration. And likewise, PFE1 has been offlined by CLI and should be restored online via CLI “request chassis…” command.
ptx10k16-01# set chassis fpc 0 pfe 0 power on
ptx10k16-01# commit
ptx10k16-01# run show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 PowerOn
1 Offlined by CLI
2 ONLINE
3 ONLINE
4 ONLINE
ptx10k16-01# run show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 RESYNC
1 Offlined by CLI
2 ONLINE
3 ONLINE
4 ONLINE
ptx10k16-01# run show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 READY
1 Offlined by CLI
2 ONLINE
3 ONLINE
4 ONLINE
ptx10k16-01# run show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 ONLINE
1 Offlined by CLI
2 ONLINE
3 ONLINE
4 ONLINE
ptx10k16-01# exit
ptx10k16-01> request chassis fpc slot 0 pfe-instance 2 online
Fru Block online initiated!
ptx10k16-01> show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 ONLINE
1 PowerOn
2 ONLINE
3 ONLINE
4 ONLINE
ptx10k16-01> show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 ONLINE
1 ONLINE
2 ONLINE
3 ONLINE
4 ONLINE
ptx10k16-01#
Just for completeness, we performed the same test without any traffic over these optic modules.
Diagram 14 Power Used on FPC0 with PFE0/1/2/3 Powered Off
Diagram 15: Power Used on the 6x SIBs with PFE0/1/2/3 Powered Off
It’s interesting to see that power is reduced on all the SIB fabric cards when we power off PFEs in the line cards.
It’s an expected behavior since the Fabric SerDes are automatically shutdown when they are facing empty slots but also facing PFE powered off as illustrated in this diagram 13.
Diagram 16: Automatic Fabric SerDes Shutdown
A PTX10001-36MR is using a single ZF Fabric ASIC, so we will expect modest power saving, but for PTX10k chassis we will have 6 SIB cards with 2, 3 or 6 ZF ASIC per fabric card depending on the form factor. In this case, we will see significantly higher power difference on the SIB side. That’s what we will now test in the second part of this article.
Diagram 19: Power Used on PTX10016 FPC0 with PFE2 and PFE3 Powered Off
Diagram 20: Power Used on PTX10016 SIBs with PFE2 and PFE3 Powered Off
PTX10008 and LC1201
Diagram 21: Power Used on PTX10008 FPC0 with PFE2 and PFE3 Powered Off
Diagram 22: Power Used on PTX10008 SIBs with PFE2 and PFE3 Powered Off
PTX10004 and LC1201
Diagram 23: Power Used on PTX10004 FPC0 with PFE2 and PFE3 Powered Off
Diagram 24: Power Used on PTX10004 SIBs with PFE2 and PFE3 Powered Off
PTX10001-36MR
Diagram 25: Power Used on PTX10001-36MR FPC0 with PFE1 and PFE2 Powered Off
Test Results
You noticed power measurement is always slightly fluctuating, that’s why we will not provide "absolute saving numbers". You can see from 120W to 135W saved per FPC when you power off a PFE (case without optics) and around 10W saved per SIB (x6). Also, we measured around 250W saved in a case with DR4 optics.
CMErrors Configured Actions
The forwarding ASICs are made of different internal blocks. In some rare occasion, errors may occur in the operational state, impacting the forwarding functionality. The Chassis Manager (CM 2.0) infrastructure is responsible for collecting faults/alarms and communicates between Routing Engine and Linecards/PFE. Based on the nature of the error, this infrastructure gives granular fault identifications: Minor, Major or Fatal. Junos Evo can be configured to define specific actions against each scope, severity, and category of error.
By default, if a Major or Fatal error occurs in PFE, the state is changed to DISABLE and all interfaces mapped to it are marked down. The PFE restart capability provides a recovery mechanism without having to reboot the entire line card or system, reducing the blast radius.
If the PFE encounters an error and gets into faulty state, the system takes specific action based on configuration.
Mode |
PTX10004 |
PTX10008 |
PTX10016 |
PTX10001-36MR |
PTX10003-80C |
PTX10003-160C |
Support |
√ |
√ |
√ |
√ |
X |
X |
Table 5: Platforms supporting CMError Configured Action
The configuration below presents the different options for the CMError action, including offline-pfe and reset-pfe. It shows how a PFE instance goes offline after CMError is injected in the PFE artificially.
ptx10k16-01# set chassis error major action ?
Possible completions:
alarm Raise FPC/SIB alarm
disable-pfe Disable PFE interfaces on FPC
get-state Retreive FPC/SIB state for debugging
log Log occurence to system log file
offline Offline FPC/SIB
offline-pfe Offline PFE on FPC
reset Reset FPC/SIB
reset-pfe Reset PFE on FPC
trap Raise FPC trap
ptx10k16-01# set chassis error major action offline-pfe
ptx10k16-01# commit
re0:
configuration check succeeds
re1:
commit complete
re0:
commit complete
ptx10k16-01# run show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 ONLINE
1 ONLINE
2 ONLINE
3 ONLINE
4 ONLINE
ptx10k16-01#
Let’s introduce a PFE error in the hardware. This is only for testing and demonstration purposes. Never execute these commands on live routers as it could lead to unexpected behaviors.
root@rtme-ptx10k16-01-fpc0:pfe> show pfe id info
First Active PFE : 0
Effective First Active PFE : 0
Number of Active PFEs : 5
Pfe Mask : 0x000000000000001f
PFEInst Down-Flags PPFE-ID PFE-State PFE-Name
------ ---------- ------------- --------- --------
0 0 0 ONLINE /Chassis[0]/Fpc[0]/Pfe[0]
0 0 1 ONLINE /Chassis[0]/Fpc[0]/Pfe[1]
1 0 2 ONLINE /Chassis[0]/Fpc[0]/Pfe[2]
1 0 3 ONLINE /Chassis[0]/Fpc[0]/Pfe[3]
2 0 4 ONLINE /Chassis[0]/Fpc[0]/Pfe[4]
2 0 5 ONLINE /Chassis[0]/Fpc[0]/Pfe[5]
3 0 6 ONLINE /Chassis[0]/Fpc[0]/Pfe[6]
3 0 7 ONLINE /Chassis[0]/Fpc[0]/Pfe[7]
4 0 8 ONLINE /Chassis[0]/Fpc[0]/Pfe[8]
root@rtme-ptx10k16-01-fpc0:pfe> show cmerror module brief
-------------------------------------------------------------------------
Module Name Active Errors PFE Callback ModuleData
Specific Function
-------------------------------------------------------------------------
1 fab-pfe@0 0 Yes 0x93963944918256 0x00000000
2 btchip 1 Yes 0x93963944918256 0x00000000
3 lkup_asic 0 Yes 0x93963944918256 0x00000000
4 PIC-0 0 No 0x93963944918256 0x00000000
5 HstLbk:pfe:2 0 No 0x93963944918256 0x00000000
6 HstLbk:pfe:4 0 No 0x93963944918256 0x00000000
7 HstLbk:pfe:0 0 No 0x93963944918256 0x00000000
8 HstLbk:pfe:1 0 No 0x93963944918256 0x00000000
9 HstLbk:pfe:3 0 No 0x93963944918256 0x00000000
root@rtme-ptx10k16-01-fpc0:pfe> show cmerror module 2
Module (2) (btchip)
PFE support 1
Get state cb 0x5575af8efdc0 platform action cb 0x5575af8efcf0 control cb (nil)
Error-id PFE Level Threshold Count Occured Cleared Last-occurred(ms ago) Name
------------------------------------------------------------------------------------------
0x450001 0 Fatal 1 0 0 0 0 hostsys_hostif_hifregs_atomic_sram_p_intr_d_perr
0x450002 0 Minor 1 0 0 0 0 hostif_dma_0_sram_p_intr_c_dma_bufmgr
0x450003 0 Minor 1 0 0 0 0 hostif_dma_1_sram_p_intr_c_dma_bufmgr
<SNIP>
root@rtme-ptx10k16-01-fpc0:pfe> test cmerror trigger-error ?
Possible completions:
<number> error_id.
root@rtme-ptx10k16-01-fpc0:pfe> test cmerror trigger-error 0x450012 ?
Possible completions:
<number> pfe_id.
root@rtme-ptx10k16-01-fpc0:pfe> test cmerror trigger-error 0x450012 0 ?
Possible completions:
<word> reason.
root@rtme-ptx10k16-01-fpc0:pfe> test cmerror trigger-error 0x450012 0 test ?
Possible completions:
<[Enter]> Execute this command
<number> module_id.
| Pipe through a command
root@rtme-ptx10k16-01-fpc0:pfe> test cmerror trigger-error 0x450012 0 test 2 ?
Possible completions:
<[Enter]> Execute this command
<number> count.
| Pipe through a command
root@rtme-ptx10k16-01-fpc0:pfe> test cmerror trigger-error 0x450012 0 test 2
The fault will be detected and the PFE will be brought offline as per the configuration:
ptx10k16-01# run show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 FAULT
1 ONLINE
2 ONLINE
3 ONLINE
4 ONLINE
ptx10k16-01# run show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 TRANSITION_OFFLINE
1 ONLINE
2 ONLINE
3 ONLINE
4 ONLINE
ptx10k16-01# run show chassis fpc pfe-instance all
FPC 0
PFE-Instance PFE-State
0 Offlined by CmError
1 ONLINE
2 ONLINE
3 ONLINE
4 ONLINE
ptx10k16-01#
The PFE state is now “Offlined by CmError” without impacting the other PFEs of the line card or the system. It will also be possible to restart it manually without collateral impact on the rest of the service.
Conclusion
The Express4 ASIC in PTX Series can be configured “power off” via CLI or configuration. It offers significant power saving on the FPC and, well applicable, on the fabric cards. Power off and restart doesn’t affect the surrounding PFEs in the system and can be also automated in case of error detection. This capability completes the long list of automated power saving features offered by default on the PTX routers. With these tools, operators can implement innovative traffic engineering rules and scripted PFE power-off to reduce the network OPEX.
Useful links
Glossary
-
CB: Control Board
-
CM Error: Chassis Manager Error is a module responsible for registering all faults generated within the different components of the Chassis
-
FPC: Flexible PIC Concentrators
-
FRU: Field Replaceable Unit
-
PFE: Packet Forward Engine
-
PIC: Physical Interface Card
-
RE: Routing Engine
-
SIB: Switch Interface Board
Acknowledgments
Thanks to Santosh Mishra, Nicolas Fevrier for their feedback and review comments on this document.