  • 1.  Junos reports powersupply problem but (show chassis environment) says all ok !!!

    Posted 02-10-2023 11:26

    Dear Juniper Experts ,

    We see a very strange alaram from our qfx5110-48s-4c ( 3 chassis - VC ) switches .

    At the same time two PSUs from diffrent chassis are not powered on .

    After checking the logs we see  no problem with the PSUs or the hardware al temperatures looks good based on the output   , Can it be a bug or maybe we are missing something ?

    I would really approcite your help on this one .

    Many thanks 

    Dave 

    #show log chassisd

    Feb 10 18:02:20  [Alarm SET] Object 75 reason 24 Device FRU PEM 1, reason PEM 1 No Power(FPC0: PEM 1 Not Powered), color 1, slot 1 Alarm id 1258356760
    Feb 10 18:02:20  send: red alarm set, device FRU PEM 1, reason FPC0: PEM 1 Not Powered
    Feb 10 18:02:22  ch_tvp_mcontrol_ipc_handler: got alarm status from member: 2
    Feb 10 18:02:22  ch_tvp_save_alarm_info ob=75, slot=2, reason=24
    Feb 10 18:02:22  send: red alarm set, device FRU PEM 1, reason FPC2: PEM 1 Not Powered
    Feb 10 18:02:25 CHASSISD_SNMP_TRAP10: SNMP trap generated: FRU power off (jnxFruContentsIndex 2, jnxFruL1Index 1, jnxFruL2Index 2, jnxFruL3Index 0, jnxFruName Power Supply 1 @ 0/1/*, jnxFruType 7, jnxFruSlot 1, jnxFruOfflineReason 2, jnxFruLastPowerOff 0, jnxFruLastPowerOn 0)
    Feb 10 18:02:25  pem_tvp_periodic cbd=950d580 slot=1, state=1
    Feb 10 18:02:25  pem_tvp_periodic cbd=950d580 slot=1, state=1
    Feb 10 18:02:25  pem_tvp_periodic cbd=951d780 slot=2, state=1
    Feb 10 18:02:25  pem_tvp_periodic cbd=951d780 slot=2, state=1
    Feb 10 18:02:25  ch_tvp_mcontrol_ipc_handler: got alarm status from member: 1
    Feb 10 18:02:25  ch_tvp_save_alarm_info ob=75, slot=1, reason=24
    Feb 10 18:02:25  send: red alarm set, device FRU PEM 1, reason FPC1: PEM 1 Not Powered
    Feb 10 18:02:26 CHASSISD_SNMP_TRAP10: SNMP trap generated: Fru Offline (jnxFruContentsIndex 2, jnxFruL1Index 3, jnxFruL2Index 2, jnxFruL3Index 0, jnxFruName Power Supply 1 @ 2/1/*, jnxFruType 7, jnxFruSlot 5, jnxFruOfflineReason 2, jnxFruLastPowerOff -1800567876, jnxFruLastPowerOn 1935977028)
    Feb 10 18:02:30  pem_tvp_periodic cbd=950d580 slot=1, state=1
    Feb 10 18:02:30  pem_tvp_periodic cbd=950d580 slot=1, state=1
    Feb 10 18:02:30  pem_tvp_periodic cbd=951d780 slot=2, state=1
    Feb 10 18:02:30  pem_tvp_periodic cbd=951d780 slot=2, state=1
    Feb 10 18:02:30 CHASSISD_SNMP_TRAP10: SNMP trap generated: Fru Offline (jnxFruContentsIndex 2, jnxFruL1Index 2, jnxFruL2Index 2, jnxFruL3Index 0, jnxFruName Power Supply 1 @ 1/1/*, jnxFruType 7, jnxFruSlot 3, jnxFruOfflineReason 2, jnxFruLastPowerOff -1800567538, jnxFruLastPowerOn 1935977516)
    Feb 10 18:02:31 CHASSISD_SNMP_TRAP6: SNMP trap generated: Power Supply failed (jnxContentsContainerIndex 2, jnxContentsL1Index 1, jnxContentsL2Index 2, jnxContentsL3Index 0, jnxContentsDescr Power Supply 1 @ 0/1/*, jnxOperatingState 6)
    Feb 10 18:02:31 CHASSISD_SNMP_TRAP6: SNMP trap generated: Power Supply failed (jnxContentsContainerIndex 2, jnxContentsL1Index 2, jnxContentsL2Index 2, jnxContentsL3Index 0, jnxContentsDescr Power Supply 1 @ 1/1/*, jnxOperatingState 6)
    Feb 10 18:02:31 CHASSISD_SNMP_TRAP6: SNMP trap generated: Power Supply failed (jnxContentsContainerIndex 2, jnxContentsL1Index 3, jnxContentsL2Index 2, jnxContentsL3Index 0, jnxContentsDescr Power Supply 1 @ 2/1/*, jnxOperatingState 6)


    #show system alarms
    2 alarms currently active
    Alarm time               Class  Description
    2023-02-10 18:02:22 UTC  Major  FPC2: PEM 1 Not Powered
    2023-02-10 18:02:20 UTC  Major  FPC0: PEM 1 Not Powered


    root@qfx01> show chassis environment
    Class Item                           Status     Measurement
    Power FPC 0 Power Supply 0           OK         53 degrees C / 127 degrees F
          FPC 0 Power Supply 1           Present
          FPC 1 Power Supply 0           OK
          FPC 1 Power Supply 1           Present
          FPC 2 Power Supply 0           OK
          FPC 2 Power Supply 1           Present
    Temp  FPC 0 Sensor TopLeft I         OK         44 degrees C / 111 degrees F
          FPC 0 Sensor TopLeft E2        OK         37 degrees C / 98 degrees F
          FPC 0 Sensor TopCenter E2      OK         39 degrees C / 102 degrees F
          FPC 0 Sensor TopLeft E1        OK         41 degrees C / 105 degrees F
          FPC 0 Sensor CPULeft I         OK         40 degrees C / 104 degrees F
          FPC 0 Sensor CPURight I        OK         39 degrees C / 102 degrees F
          FPC 0 Sensor CPU Die Temp      OK         49 degrees C / 120 degrees F
          FPC 0 Sensor TopRight OCXO     OK         39 degrees C / 102 degrees F
          FPC 0 Sensor TopRight E        OK         41 degrees C / 105 degrees F
          FPC 0 Sensor BottomLeft E      OK         42 degrees C / 107 degrees F
          FPC 0 Sensor TopRight I        OK         34 degrees C / 93 degrees F
          FPC 0 Sensor TopCenter E1      OK         39 degrees C / 102 degrees F
          FPC 1 Sensor TopLeft I         OK         42 degrees C / 107 degrees F
          FPC 1 Sensor TopLeft E2        OK         35 degrees C / 95 degrees F
          FPC 1 Sensor TopCenter E2      OK         37 degrees C / 98 degrees F
          FPC 1 Sensor TopLeft E1        OK         40 degrees C / 104 degrees F
          FPC 1 Sensor CPULeft I         OK         38 degrees C / 100 degrees F
          FPC 1 Sensor CPURight I        OK         38 degrees C / 100 degrees F
          FPC 1 Sensor CPU Die Temp      OK         48 degrees C / 118 degrees F
          FPC 1 Sensor TopRight OCXO     OK         38 degrees C / 100 degrees F
          FPC 1 Sensor TopRight E        OK         40 degrees C / 104 degrees F
          FPC 1 Sensor BottomLeft E      OK         40 degrees C / 104 degrees F
          FPC 1 Sensor TopRight I        OK         32 degrees C / 89 degrees F
          FPC 1 Sensor TopCenter E1      OK         37 degrees C / 98 degrees F
          FPC 2 Sensor TopLeft I         OK         40 degrees C / 104 degrees F
          FPC 2 Sensor TopLeft E2        OK         35 degrees C / 95 degrees F
          FPC 2 Sensor TopCenter E2      OK         34 degrees C / 93 degrees F
          FPC 2 Sensor TopLeft E1        OK         38 degrees C / 100 degrees F
          FPC 2 Sensor CPULeft I         OK         36 degrees C / 96 degrees F
          FPC 2 Sensor CPURight I        OK         36 degrees C / 96 degrees F
          FPC 2 Sensor CPU Die Temp      OK         49 degrees C / 120 degrees F
          FPC 2 Sensor TopRight OCXO     OK         37 degrees C / 98 degrees F
          FPC 2 Sensor TopRight E        OK         37 degrees C / 98 degrees F
          FPC 2 Sensor BottomLeft E      OK         37 degrees C / 98 degrees F
          FPC 2 Sensor TopRight I        OK         30 degrees C / 86 degrees F
          FPC 2 Sensor TopCenter E1      OK         34 degrees C / 93 degrees F
    Fans  FPC 0 Fan Tray 0               OK         Spinning at normal speed
          FPC 0 Fan Tray 1               OK         Spinning at normal speed
          FPC 0 Fan Tray 2               OK         Spinning at normal speed
          FPC 0 Fan Tray 3               OK         Spinning at normal speed
          FPC 0 Fan Tray 4               OK         Spinning at normal speed
          FPC 1 Fan Tray 0               OK         Spinning at normal speed
          FPC 1 Fan Tray 1               OK         Spinning at normal speed
          FPC 1 Fan Tray 2               OK         Spinning at normal speed
          FPC 1 Fan Tray 3               OK         Spinning at normal speed
          FPC 1 Fan Tray 4               OK         Spinning at normal speed
          FPC 2 Fan Tray 0               OK         Spinning at normal speed
          FPC 2 Fan Tray 1               OK         Spinning at normal speed
          FPC 2 Fan Tray 2               OK         Spinning at normal speed
          FPC 2 Fan Tray 3               OK         Spinning at normal speed
          FPC 2 Fan Tray 4               OK         Spinning at normal speed


    {master:0}
    # root@qfx01> show chassis environment pem
    localre:
    --------------------------------------------------------------------------
    FPC 0 PEM 0 status:
      State                      Online
      Airflow                    Front to Back
      Temp Sensor 0              OK   53 degrees C / 127 degrees F
      Temp Sensor 1              OK   29 degrees C / 84 degrees F
      Temp Sensor 2              OK   23 degrees C / 73 degrees F
      Fan 0                      4680 RPM
      Fan 1                      4680 RPM
      DC Output           Voltage(V) Current(A)  Power(W)  Load(%)
                            12          10            120      18
    FPC 1 PEM 0 status:
      State                      Online
      Airflow                    Front to Back
      Temperature                OK
      DC Output           Voltage(V) Current(A)  Power(W)  Load(%)
                            12          10            120      18
    FPC 2 PEM 0 status:
      State                      Online
      Airflow                    Front to Back
      Temperature                OK
      DC Output           Voltage(V) Current(A)  Power(W)  Load(%)
                            12          9             108      16

    fpc1:
    --------------------------------------------------------------------------
    FPC 1 PEM 0 status:
      State                      Online
      Airflow                    Front to Back
      Temp Sensor 0              OK   46 degrees C / 114 degrees F
      Temp Sensor 1              OK   38 degrees C / 100 degrees F
      Temp Sensor 2              OK   30 degrees C / 86 degrees F
      Fan 0                      4140 RPM
      Fan 1                      3960 RPM
      DC Output           Voltage(V) Current(A)  Power(W)  Load(%)
                            12          10            120      18

    fpc2:
    --------------------------------------------------------------------------
    FPC 2 PEM 0 status:
      State                      Online
      Airflow                    Front to Back
      Temp Sensor 0              OK   52 degrees C / 125 degrees F
      Temp Sensor 1              OK   29 degrees C / 84 degrees F
      Temp Sensor 2              OK   22 degrees C / 71 degrees F
      Fan 0                      4140 RPM
      Fan 1                      3900 RPM
      DC Output           Voltage(V) Current(A)  Power(W)  Load(%)
                            12          10            120      18



    ------------------------------
    David Rad
    ------------------------------



  • 2.  RE: Junos reports powersupply problem but (show chassis environment) says all ok !!!

    Posted 02-11-2023 11:19

    The show commands say that on the 3 switches, Power Supply 0 is «OK» whereas Power Supply 1 is «Present», and there's no power delivered by the three PEM 1.

    Seems like one power source is on (with all the PEM0 plugged on it) and the other one is off (with all the PEM1) in your rack.



    ------------------------------
    Olivier Benghozi
    ------------------------------



  • 3.  RE: Junos reports powersupply problem but (show chassis environment) says all ok !!!

    Posted 02-11-2023 13:17
    Dear Olivier,
    Many thanks for your reply !
    We have found indeed that all seems to be okay with the psus on all switches , the problem as it seems was with the power outage with one of the power lines and it's back to normal .
    Again I would like to thank you that you took time to reply my question.
    Best regards,
    Dave