  • 1.  Mx204 showing one psu absent when both psu are working fine

    Posted 03-04-2022 10:31

    Hello,

    We are getting strange output of command when we execute wo commands for chassis hardware.

    Model: mx204
    Junos: 20.3R1.8
    When we run #run show chassis hardware
    PEM 1 REV xxxxxxxxxxxxxxxxxx    JPSU-650W-AC-AO


    run show chassis environment
    Power PEM 0 Absent
    PEM 1 OK 31 degrees C / 87 degrees F

    But both PSU are plugged in and showing green active light.
    Any idea why Mx204 not showing both psu active?

    Thanks



  • 2.  RE: Mx204 showing one psu absent when both psu are working fine

    Posted 03-04-2022 12:34
    Hi,
    what Junos version run on your MX204?

    ------------------------------
    FRANCESCO ONERI
    ------------------------------



  • 3.  RE: Mx204 showing one psu absent when both psu are working fine

    Posted 03-05-2022 06:41
    Model: mx204
    Junos: 20.3R1.8


  • 4.  RE: Mx204 showing one psu absent when both psu are working fine

     
    Posted 03-04-2022 12:34
    Are you sure it's installed in the chassis fully? Does it work while plugged into slot PEM1?


  • 5.  RE: Mx204 showing one psu absent when both psu are working fine

    Posted 03-05-2022 06:41
      |   view attached
    Hello,
    Yes it is installed. See attachment.
    Thanks in advance.


  • 6.  RE: Mx204 showing one psu absent when both psu are working fine

    Posted 03-07-2022 05:50
    Do you have any alarms that might give more information?

    show chassis alarms
    show system alarms

    ------------------------------
    Steve Puluka BSEET - Juniper Ambassador
    IP Architect - DQE Communications Pittsburgh, PA (Metro Ethernet & ISP)
    http://puluka.com/home
    ------------------------------



  • 7.  RE: Mx204 showing one psu absent when both psu are working fine

    Posted 03-07-2022 09:38
    Edited by Michael Pappas 03-08-2022 09:54
    Hi,
    we had the same problem in the past.
    We had fixed it with upgrade to Junos: 20.4R3.8.
    Regards
    -------------------------------------------
    Original Message:
    Sent: 3/7/2022 5:50:00 AM
    From: spuluka
    Subject: RE: Mx204 showing one psu absent when both psu are working fine

    Do you have any alarms that might give more information?

    show chassis alarms
    show system alarms

    ------------------------------
    Steve Puluka BSEET - Juniper Ambassador
    IP Architect - DQE Communications Pittsburgh, PA (Metro Ethernet & ISP)
    http://puluka.com/home
    ------------------------------



  • 8.  RE: Mx204 showing one psu absent when both psu are working fine

    Posted 03-07-2022 09:38
    Hello,
    Both command shows
    No alarms currently active

    Thanks