  • 1.  EX4300 switch

    Posted 01-21-2021 17:50

    We are upgrading our IDF closet with a new cooling AC systems and they wanted to know how much heat is being generated by the ex4300 switch ? 

    Is there any documentation out there or formula to figure out how much heat the switch puts out?

    There is a virtual chassis in the IDF room made of total of 6 switches

    Thanks
    GXS


  • 2.  RE: EX4300 switch

    Posted 01-22-2021 02:41
    Edited by StephA 01-22-2021 02:41
    It depends if you have POE 

    referring to EX4300 Site Guidelines and Requirements - TechLibrary - Juniper Networks

    it goes from 423 BTU/hour up to  5844 BTU/hour.







  • 3.  RE: EX4300 switch

    Posted 01-22-2021 08:38
    Thanks StepA for the info I appreciate it.